Duplicate active TCP sockets generated by a single `Modbus_TCP_Slave`
3 hours 8 minutes ago #420
by Eduardo
Environment Specs:
) after a cold boot, the main PLC process (
) opens two simultaneous active TCP sockets to the Modbus gateway IP
. Both sockets actively transmit identical Modbus TCP request streams in parallel, causing frame collisions and delays on the underlying RS-485 serial bus.Diagnostic Evidence:1. Socket Inspection ( ss -tnp )
Both
and
continuously fluctuate on both file descriptors (fd=4 and fd=6), proving that both sockets are actively exchanging traffic with the gateway (neither socket is idle or hanging).2. Payload Analysis ( tcpdump )Decoding the Modbus TCP application layer reveals a 1:1 mirror traffic pattern between local ports
and
:
- ProviewR Version: 6.1.5
- OS: Linux (Debian 12 / Linux Mint)
- Node / Bus: Development Node under Bus 999 (
)Code:plc_wicotas_0999_plc
- Modbus Gateway: Exemys EGW1 (Modbus TCP to RS-485 converter, IP
)Code:10.59.1.50:502
- Slave Devices: Micro Motion RFT9739 (Unit ID 1), Micro Motion 1700 MVD (Unit ID 3)
Code:
rt_ini &
Code:
plc_wicotas_0999_plc
Code:
10.59.1.50:502
Code:
ESTAB 0 0 10.59.1.2:60178 10.59.1.50:502 users:(("plc_wicotas_0999_plc",pid=25050,fd=4))
ESTAB 0 24 10.59.1.2:60180 10.59.1.50:502 users:(("plc_wicotas_0999_plc",pid=25050,fd=6))
Code:
Send-Q
Code:
Recv-Q
Code:
60178
Code:
60180
- Port 60178: Transmits
(Read Holding Registers for PDU 246, 258, 244, 1) andCode:FC03(Write Single Coil 3) to Unit ID 1 and Unit ID 3.Code:FC05
- Port 60180: Transmits identical
andCode:FC03request bursts to Unit ID 1 and Unit ID 3 at the exact same intervals.Code:FC05
- There is strictly one Modbus_Master and one Modbus_TCP_Slave object under
.Code:wicoTAS ➔ IO
- A single
(Code:PlcThread) is defined and assigned.Code:Plc1
- Attribute
is set uniformly across allCode:Process = 1 (PLC)objects.Code:Modbus_Module
- A clean build (
+Code:Clean Volume) was performed, but two sockets continue to open automatically on runtime startup.Code:Build Node
- Why does the PLC runtime engine instantiate two independent TCP sockets (
andCode:fd=4) for a singleCode:fd=6object?Code:Modbus_TCP_Slave
- Does ProviewR separate cyclic transactions (
) from triggered transactions (Code:Continuous = YES) into dedicated sockets, or isCode:Continuous = NObeing called twice within the multithreaded framework?Code:io_init()
- What is the recommended configuration to force ProviewR to multiplex all Modbus TCP requests over a single TCP socket descriptor?
Please Log in or Create an account to join the conversation.
2 hours 54 minutes ago #421
by Eduardo
Replied by Eduardo on topic Duplicate active TCP sockets generated by a single `Modbus_TCP_Slave`
Apologies for the formatting issue in the main post!** The forum editor automatically parsed the inline code tags into `Code:` blocks and split some lines, and I am unable to edit the original thread.
To summarize the core environment and issue cleanly:
**PLC Process:** `plc_wicotas_0999_plc` (Bus 999)
**Target Gateway:** Exemys EGW1 (`10.59.1.50:502`)
**Slaves:** Micro Motion RFT9739 (ID 1) & Model 1700 (ID 3)
**Issue:** Executing `rt_ini &` automatically opens two active TCP sockets (`fd=4` and `fd=6`) from the exact same process (`pid=25050`) to `10.59.1.50:502`, sending 1:1 identical Modbus TCP request bursts.
Thank you for your understanding and any guidance on how to resolve this duplicate socket behavior!
To summarize the core environment and issue cleanly:
**PLC Process:** `plc_wicotas_0999_plc` (Bus 999)
**Target Gateway:** Exemys EGW1 (`10.59.1.50:502`)
**Slaves:** Micro Motion RFT9739 (ID 1) & Model 1700 (ID 3)
**Issue:** Executing `rt_ini &` automatically opens two active TCP sockets (`fd=4` and `fd=6`) from the exact same process (`pid=25050`) to `10.59.1.50:502`, sending 1:1 identical Modbus TCP request bursts.
Thank you for your understanding and any guidance on how to resolve this duplicate socket behavior!